• Greetings from the GeneralPAC Team!

    FIRST EVER GENERALPAC GIVEAWAY!

    Hello there Everyone!

    The wait is over! Through your love and support we have reached 13.5k and as a token of gratitude, we are thrilled to announce our FIRST EVER GIVEAWAY! We are also nearing our Patreon Channel’s first anniversary (in the month of April) so the prize is related to that!

    THREE lucky winners can now win PATREON ACCESS worth $50 for FREE! Isn’t that just unbelievable?

    You can watch complete tutorials on your favorite series without the hassle of signing up for our Patreon page.

    But every prize needs some effort so here some tasks to qualify for the prize! Entering the giveaway in 5 simple steps and win it.

    An example of a comment: Great tutorials on power system topics. Keep it up. All tasks are done! Can you do a video on per-unit systems? #GeneralPAC #PowerSystemTutorials Facebook username: gpac.2019 YouTube username/channel name: gpac2019

    The link of the video is here : GeneralPac giveaway video

Does a numerical/digital o/c relay act on rms or instatantenous current values ?

DJme

New Member
#1
I have really benefited from your videos, you guys rock !

I am having a hard time understanding a little detail of how numerical/digital overcurrent relays work. Supposing I set a relay to trip at 400 amperes primary current after a time delay of 30ms, given that AC current rises from zero to the peak positive value, drops back to zero and rises to the peak negative value, it's possible that the current exceeds 400 only for a part of both the negative and positive cycles.

How does the relay determine that the trip condition has been met ? does it act based on the rms value of the current ?
I hope someone can understand what I am trying to pass across, I can provide a diagram to explain better if need be.

Thanks.
 

arrehman1

Administrator
Staff member
#2
Hi @DJme

This is a great question and one that we're open to creating a video one. We can't answer your question directly but we will point you in the right direction. Hopefully our response is useful to you and others.

According to this paper by Zocholl: How Microprocessor Relays Respond to Harmonics, Saturation, and Other Wave Distortions

What do relays measure? Electromechanical relays produce torque that is proportional to the square of the flux produced by current. These relays respond to the current squared or to the product of the currents produced by the input quantities. Since root-mean-square (rms) is defined as
the average of the integral of the square of the current, these relays are said to be rms responsive.

Solid-state analog relays, utilizing linear circuits and level detectors, respond to the peak of the input signal. Where microprocessor relays can implement either of these techniques, most microprocessor relays use digital filters to extract only the fundamental and either attenuate or
eliminate harmonics.


The key to the behavior of microprocessor relays is the output of the digital filter. This is obtained by sampling sine-wave currents and/or voltages at discrete time intervals. A fixed number of instantaneous samples per cycle are converted to digital quantities by an A/D converter and stored for processing. Digital filtering is the simple process of multiplying the successive samples by predetermined coefficients and then combining
them to obtain digital quantities representing the phasor components of the input.

Also, according to the SEL 751 Relay manual, the phase instantaneous overcurrent elements normally operate by using the output of the one cycle cosine filtered phase current. During severe CT saturation, the cosine-filtered phase current magnitude can be substantially reduced because of the high harmonic content and reduced magnitude of the distorted secondary waveform. If the overcurrent element relied only on the output of the cosine-filtered secondary current, the operation of any high-set instantaneous overcurrent element might be severely delayed and jeopardized so that's why the bipolar peak dectector is also used for highset inst elements. Read the manual (section 4.12) on this for more detail.


Further in to the manual (section 10.17), Figure 10.4 and Figure 10.5 look in detail at one cycle of A-phase current (channel IA) identified in Figure 10.3. Figure 10.4 shows how the event report ac current column data relate to the actual sampled waveform and rms values. Figure 10.5 shows how the event report current column data can be converted to phasor rms values. Voltages are processed similarly.

1547322250627.png


In Figure 10.5, note that you can use two rows of current data from the event report in Figure 10.3, 1/4 cycle apart, to calculate phasor rms current values. In Figure 10.5, at the present sample, the phasor rms current value is:

1547322313471.png

The present sample (IA = 940.7 A) is a real rms current value that relates to the phasor rms current value:

1547322327607.png

1547322490163.png

I have attached the paper to this post which is publicly available. You can download the SEL 751 relay Manual here. You should definitely use SEL resource as they are very useful and credible. If you find this post useful or valuable, please consider subscribing and donating to https://www.patreon.com/join/generalpac so we can continue making high-quality video tutorials and respond to questions like this one.